    Dear Team

     

    Kindly see the concerns raised on the metrics currently monitored on power devices by the EMS solution (spectrum)

     

    Please note that the EMS Monitoring solution only picks minor fault but do not pick the major faults in the power devices

     

    Please see minor faults on the devices (UPS and Inverters) below;

    • Equipment unreachable due to network problem

     

    Major faults on the power devices;

    • Devices running on battery,
    • Devices Component/parts fault/failure,
    • Devices High room temperature,

     

    Kindly advise promptly in order to resolve and track all major faults going forward

     

    Regards,



  • 2.  Re: Regularization of the metrics being monitored on power devices
    Best Answer

    Posted May 26, 2017 11:29 AM

    Hello,

     

    If your UPS/Inverter is capable of sending TRAP alerts to Spectrum, you simply need to MAP those TRAP into Spectrum EVENTs/Alarms using MibTools.

     

    see Wiki

    Trap Support for MIB Objects - CA Spectrum - 10.2 and 10.2.1 - CA Technologies Documentation 

     

    Adam